This was the biggest claim of my career as a casualty claim adjuster.
I handled nothing but Hyatt claims for more than a year.
I remember that incident. At the time I was working as a structural steel detailer, which entails translating engineers’ plans into detailed drawings of each piece of steel. For instance, every steel beam in a high-rise building is detailed, showing how many and what size bolts to use and where to drill the holes in the beam, so the building goes together like an erector set. The engineers’ plans give the load and stress for each connection and the size of the beams, and the detailer calculates (using a large book of tables which I assume is digitized these days) the size and number of the bolts etc. Of course all the “drawing” is now computerized as well. But in the days of the above incident it was all still done by hand.I seem to remember reading about that one. If I recall correctly, they had the walkways hanging from the ceiling at two levels, and the structural design called for a single, continuous hangar rod, passing through both walkways with a bolt and bracket supporting each walkway at that point.
The builders installed two hangar rods, one supporting the upper walkway from the ceiling, and the second supporting the lower walkway from the upper walkway.
They reasoned that the total load on the hangar rods was, of course, the same in both cases, so (as the rods were rated for that load) this change didn't require structural engineer approval.
However they failed to consider the load on the bolts. In the original design, each bolt and bracket carried the load of the one walkway it supported; But in the new design, the bolt supporting the upper walkway now carried the full combined load from both walkways. Now under up to twice its design loading, it inevitably failed when fully loaded.
Which is why we don't let unqualified people do structural engineering assessments. This has become a classic example of how easy it is to overlook something critical, and is now used for training builders, engineers and achitects.
As an engineer friend of mine remarked, engineers need to be more careful than doctors, because a doctor who makes a mistake might kill somebody, but an engineer who makes a mistake might kill hundreds.
(I don't watch online video, so my apologies if that's not the same event you are talking about).
Reminds me of the Westgate Bridge Collapse. There was a royal commission into the collapse. One recommendation was that the review of all calculations must be more rigorous and use some engineers from outside the main architects and builders.I seem to remember reading about that one. If I recall correctly, they had the walkways hanging from the ceiling at two levels, and the structural design called for a single, continuous hangar rod, passing through both walkways with a bolt and bracket supporting each walkway at that point.
The builders installed two hangar rods, one supporting the upper walkway from the ceiling, and the second supporting the lower walkway from the upper walkway.
They reasoned that the total load on the hangar rods was, of course, the same in both cases, so (as the rods were rated for that load) this change didn't require structural engineer approval.
However they failed to consider the load on the bolts. In the original design, each bolt and bracket carried the load of the one walkway it supported; But in the new design, the bolt supporting the upper walkway now carried the full combined load from both walkways. Now under up to twice its design loading, it inevitably failed when fully loaded.
Indeed they do.As an engineer friend of mine remarked, engineers need to be more careful than doctors, because a doctor who makes a mistake might kill somebody, but an engineer who makes a mistake might kill hundreds.